Start by calculating the design current
Select an MCB which is higher than that of the design current
Apply the correction factors to the size of the MCB
Use this to select a cable from the appendix of the regs
Verify the volt drop doesn't exceed the maximum allowed
If the cpc is the same size as the lives then it is fine
If the cpc is smaller then you can check it with regulation 543.1 in the regs.