by Jeffmo »
Thu May 24, 2007 9:42 pm
cookers are usually protected by a 30 amp fuse or mcb for a cooker rated at up to 12kw and a 45 amp fuse or 50 amp mcb is needed for a cooker rated at above 12kw.So initially check the rating of the cooker , i am a bit suspicious about the fuse rating , reason being 30 amp really only needs 6mm cable up to 20 metres and 10mm cable if the run is between 20 and 30 m , i have a feeling that the protection is too small . Another possible is inside the cooker connection box or cooker switch there is a loose connection . If the switch incorporates a 13amp socket opening then they are notorious for loose conns , due to the amount of cable chucked in the back of them , especially with the larger cables from 10 mm up . Remember though please be very safety concious if your having a look . I think for someone whose not sure its best to get someone in .Hope this helps , you will probably get a reply from my guru of electricity Mr Sparks as well , he is the man so listen good . Good luck Jeff