I have just move into a bungalow that was built 50 years ago and extended in the early 70s.

Last night I discovered that in order to isolate the power from the sockets you need to pull two 15Amp fuses.

If you pull just one the sockets stay live, it does not matter which one you pull.

Therefore the two fuses are in parallel, this seams wrong - is it?

Posted: Tue Apr 07, 2009 6:14 pm
by kbrownie
MuddyFunkster,
It is wrong you have Ring final circuit and someone has decided to run each leg of a different fuse/breaker!
This a not safe or good method :shock:
It needs to be in one fuse/breaker only
What size cable is it and what area does the circuit cover in square meters?
Then we can advise correct fuse size.
KB

Posted: Tue Apr 07, 2009 6:56 pm
by kuzz
very wrong and very dangerous. It could be very simple to fix, or it could be more complex, either way you'll need an electrician with a set of test equipment.

Posted: Tue Apr 07, 2009 9:50 pm
by rosebery
It sounds to me as though a PIR would be money very well spent on your electrical installation.