Wiring kitchen fixed appliances
Ask questions and find answers to many subjects relating to electrics and electrical work

6 posts   •   Page 1 of 1
spinkox
Apprentice
Apprentice
Posts: 11
Joined: Wed Feb 04, 2009 6:14 pm

Wiring kitchen fixed appliances

by spinkox » Sun Jun 14, 2009 2:26 pm

Can you tell me if it is acceptable to have sockets for appliances such as fridge, washing machine and cooker fixed into standard chipboard cupboards below the work top.

Also do these appliances have to be hard wired into a fused connection unit or can they just be plugged in . . .

Thanks - steve

kbrownie
Project Manager
Project Manager
Posts: 1995
Joined: Mon Mar 05, 2007 9:36 pm

by kbrownie » Mon Jun 15, 2009 10:06 am

spinkox, when appliances are fixed in to units and not stand alone appliances,
you will find the carcass is free of back board and a socket outlet is installed in/on wall behind. If it is integral/fixed appliance the socket outlet should be connected to a switched FCU above the work top, to offer isolation.
Work in kitchen needs to comply to part P of building regs or be installed by domestic installer registered electrician.
KB

spinkox
Apprentice
Apprentice
Posts: 11
Joined: Wed Feb 04, 2009 6:14 pm

by spinkox » Sun Jun 21, 2009 10:25 am

Thanks for your reply . . .

If they are not integral/fixed appliances - such as a washing machine or fridge which comes as standard with a 3pin plug attached - presumably they are allowed to be plugged into a socket in the normal way. Can this socket be fixed to the chipboard cubboard below the work top??

steve

kbrownie
Project Manager
Project Manager
Posts: 1995
Joined: Mon Mar 05, 2007 9:36 pm

by kbrownie » Sun Jun 21, 2009 8:07 pm

It's not the best way to fix a socket-outlet, if ever the cupboard was removed the socket would be no longer secure.
Stick it on the wall, normally the backs of the kitchen units where washing machines etc.. are installed are removed for pipework and socket.
Installing any new, additional or extension to electrical circuits in kitchens comes under part p read projects or it should be done by registered electrician.
KB

moggy1968
Ganger
Ganger
Posts: 198
Joined: Sat Feb 21, 2009 11:32 am

by moggy1968 » Mon Jun 22, 2009 9:42 pm

also it must be possible to isolate the appliance without moving it, even if it is plugged in. so if your socket is behind your fridge you need a seperate isolator.
genrally sockets should be mounted on a permanent structure. there is a degree of interpretation as to wether that means cupboard backs!

spinkox
Apprentice
Apprentice
Posts: 11
Joined: Wed Feb 04, 2009 6:14 pm

by spinkox » Thu Jun 25, 2009 9:34 am

OK that all makes sense - Thanks for your help . . .

steve