ring mane trips

Posted: Fri Jul 31, 2009 7:28 pm
by jamespond1
hi, i have installed a ring main upstairs and one downstairs. the problem is my downstairs ring is tripping the rcd, i have checked all 9 sockets all cables are correct and earths insulated i have used a fluke to check the ring is correct and i do get continuity. can some body give me any advice.
many thanks james.

Posted: Sat Aug 01, 2009 3:40 pm
by kbrownie
Have you notified building controls under part p installing a new circuit

Posted: Sat Aug 01, 2009 5:41 pm
by sparx
Have you checked Neutrals on same RCD supply as lives for ring? presume you have split load board with 2 rcd's
If not that then check for N-E fault, often front plate screw of socket pressing on N in back box,
regards Sparx