16a blue socket
Posted: Wed Aug 05, 2009 8:18 am
by fisha
hi guys can anyone tell me if i can keep a standard 13a socket and a blue 16a socket on the same circuit or is it better to keep them on seperate circuits and use a type c mcb for the 16a sockets, any advice would be great
Posted: Wed Aug 05, 2009 6:47 pm
by kbrownie
What you doing?
What is it 16amp site comando type socket
Posted: Wed Aug 05, 2009 9:49 pm
Hi, I would keep them separate. Blue sockets not having fused plugs are limited to 16A mcb on radial but 13A circuits usually 20/32A circuits with more than one outlet per circuit.
Posted: Thu Aug 06, 2009 12:31 am
by fisha
thanks for the info , is it always 1 16amp socket to 1 mcb so. i presume it is advised to use a type c mcb for the 16amp sockets
Posted: Thu Aug 06, 2009 8:41 pm
type of mcb will be determined by your Zs on the far end of run to socket, type C will limit it to 1.15 ohms, but type B will allow up to 2.29 ohms, always go for a B over a C type for closer protection unless large starting surge of whatever is plugged in causing mcb to trip,
regards Sparx
Posted: Fri Aug 07, 2009 8:55 am
by fisha
thanks sparx, its a 16 a blue socket brownie, all the sockets will be within 10m of each other, can i put more than one 16a socket on the same circuit, or does each 16a socket need a seperate mcb, also i was wondering can i put a standard 13a socket on the same circuit as a 16a amp socket, thanks browie and sparx