Ceiling downlights

Posted: Tue May 29, 2007 12:30 am
by JohnK
Hi, First post, New build, Elect. has left site and left ceiling terminal blocks in roof space for downlights to be fitted. Have installed them using flat 1.0mm twin cable - do I need to clip all of these cables to meet the regs?

In bathroom moved single ceiling terminal box to roof space and replaced with 4 terminal junction box, and tailed out to downlights - suitable for Zone 1. Is this OK?

Many thanks

Posted: Wed May 30, 2007 8:03 pm
by Jeffmo
hi , cables need to be 50mm above ceiling and 50mm below floor , if running with joists then these cables need to be clipped not exceeding 250mm , obviously against joists then either place cables in earthed steel conduit and notch out top of joists or drill through joists in centre line , maximum diameter 0.25 x joist depth .Hope this helps good luck . Regards Jeff

Posted: Wed May 30, 2007 9:06 pm
by sparx
Hi, yes should run cables where they won't be liable to damage, ie clipped to sides of timbers, in eaves etc,
J.B to lights fine , make sure cable outer sheath is in clamps of d/lighters, not just cores other wise all OK
regards SPARX

Posted: Sat Jun 02, 2007 3:03 pm
by JohnK
Many thanks for all your help