Granny Annexe
Posted: Tue Mar 23, 2010 8:03 pm
Hi all,
Only basics now i'm afraid.
Main house max demand 210a with diversity.
Granny annexe 115a with diversity.
I recommended extra phase to supply annexe as it will be ran as a new house by mother-in-law.
Not happy with that, they had second opinion and now have split tails with sub CU supplying annexe 25m away on 16mm2 T&E.
So 100a supply cutout, 114a 25mm2 tails, splitter box 100a max, meter 100a and overhaed cables 100a (as per e on) supplying two houses. Combined max demand after diversity 325a. Don't like what has been done. LABC inspecting and testing as I have walked. My concern is a family being cooked due to overloaded supply cables, tails, meter, splitter box.
I know this is basic but I can't write it all again as my will to live has been tested already.
Any opinions are very welcome.
Kind regards
Jackhawk
Only basics now i'm afraid.
Main house max demand 210a with diversity.
Granny annexe 115a with diversity.
I recommended extra phase to supply annexe as it will be ran as a new house by mother-in-law.
Not happy with that, they had second opinion and now have split tails with sub CU supplying annexe 25m away on 16mm2 T&E.
So 100a supply cutout, 114a 25mm2 tails, splitter box 100a max, meter 100a and overhaed cables 100a (as per e on) supplying two houses. Combined max demand after diversity 325a. Don't like what has been done. LABC inspecting and testing as I have walked. My concern is a family being cooked due to overloaded supply cables, tails, meter, splitter box.