Kitchen Ring Main
didster
Kitchen Ring Main
by didster » Mon Sep 05, 2011 9:01 pm
Hi there,
We are having a new kitchen fitted by a UK DIY store where they are supplying both the kitchen and the fitters. They are insisting that we require a new dedicated ring main installed for the kitchen which is almost doubling the installation costs. Currently, we have enough sockets in the kitchen to run everything we need, all running from the main house ring. All the sockets are in the place they would need to be and run a microwave, kettle, tumble dryer and fridge. There is also a dedicated supply for the cooker and another one for the hob, both on 6mm cables with 32a MCBs.
Could someone please confirm/deny that it is a REGULATION that new kitchen installations must be on their own ring, or simply a recommendation? They are also saying that this new ring is going to be installed using trucking as taking the floor boards up will take much longer - which is somewhat annoying in a newly plastered kitchen!
Many thanks
Re: Kitchen Ring Main
by ericmark » Tue Sep 06, 2011 7:11 am
There is nothing to say a kitchen should have a dedicated final ring or any sub-main however it does say:-
RING FINAL CIRCUIT ARRANGEMENTS, REGULATION 433.1.5
The load current in any part of the circuit should be unlikely to exceed for long periods the current-carrying capacity of the cable (Regulation 433.1.5 refers). This can generally be achieved by:
(i) locating socket-outlets to provide reasonable sharing of the load around the ring
(ii) not supplying immersion heaters, comprehensive electric space heating or loads of a similar profile from the ring circuit
(iii) connecting cookers, ovens and hobs with a rated power exceeding 2 kW on their own dedicated radial circuit
If one was to take this rule by the letter the whole idea of having a bank of switches marked tumble drier, washing machine, etc. coming from a dedicated kitchen ring would be out and each switch should have it's own radial circuit in the same way as a cooker does.
In practice the running of washing machine, tumble drier, from the ring is still done even if it does not strictly comply.
However there is one problem which haunts many of an electrician and that is anything new must comply with latest regulations so when adding sockets to a non RCD protected circuit one has to include RCD protection. One socket is easy just use Ali-tube cable and a RCD socket or run the cable surface and use a RCD socket. Problem being that unless the special Ali-Tube to BS 8436 Guardian, Earthshield, or Flexishield, Afumex, according to manufacturer rated 90 deg C is used then either the cable has to be RCD protected or run through metal conduit if buried in the wall. So using trunking means they don't have to use Ali-tube.
The problem with Ali-tube is it's not only slightly more expensive but often can only be bought by the role. Unlike twin and earth where one can buy 5 meters from B&Q one often has to buy 100 meters. In theory for an electrician this should be no problem as he will in the end use it. But most jobs using any length of cable will have RCD protection so he would have it on his hands for a long time and as I said it's expensive.
So in the main electricians try not to buy a role and use surface wiring where to bury cable would require use of Ali-tube.
It is not only the electrician but also the client as of course it is far cheaper to surface mount cable. And with a kitchen often with a little thought cables can be hidden with the units fitted.
The regulations are designed for all and so do not say you must fit a dedicated radial or ring but say it in a more roundabout way so where used in special situations one has multiple ways to comply.
It is very easy to make an error when commenting on something like this. A washing machine, and tumble drier are not kitchen appliances (even though often are in a kitchen) and the dishwasher is not used in all kitchens so with dedicated supplies for hob and oven one could very well have nothing exceeding 2kW and also have RCD protection on all circuits which would likely mean the only loads onto the ring are from portable appliances like the kettle. In which case no need for new supply for kitchen.
However if going by the letter and you need dedicated supplies for washing machine, tumble drier, and dishwasher, (All normally over 2kW) then running three extra radials back to the consumer unit will likely present problems maybe even require a new consumer unit. One way used to get around the problem is to run SWA cable around outside of house to the incoming supply and have a mini consumer unit in the kitchen. There are some advantages with this in that also it doubles as local isolator so no need to fit grid switches to isolate the washing machine. (If you have ever seen one when the weights come lose you would never consider fitting one under counter without local isolator).
However under the Part P regulations the electrician if part of a scheme has to sign for design, installation and testing you are not permitted to undertake one of the three functions. To have separate signatories one would need to register the work with LABC which again would cost. So to get any other system installed you have to persuade the electrician that he should change his design. One would hope he is flexible and open to suggestions but he is signing the paperwork so it's his call.
I will guess RCD protection is the problem but you don't say if circuits are RCD protected or not.
didster
by didster » Tue Sep 06, 2011 9:11 am
Many thanks for the great reply.
The circuits are RCD protected. A new dual rcd consumer unit was put in only last year. Does that mean the cables don't have to be run though conduit within the wall? Many are not and are just chased in. In fact, I remember the sparky that did the CU replacement doing just this - he just went over the top with some bonding...
I can't help thinking they are just wanting to do work for the sake of doing it. No one from their has actually inspected our kitchen, but they are insistent that a new ring is put in before their fitters can start.
We are going to try someone else this weekend, hopefully they wont say the same thing!
by ericmark » Wed Sep 07, 2011 1:25 am
Conduit and capping are very different and conduit is rare in newer houses. And yes with a RCD no need for conduit. Capping is only to stop the plaster from damaging the cables.
[quote]No one from their has actually inspected our kitchen[/quote]
So how would they know if anything needed up-grading? Seems a little odd!
I was rather surprised to find in Germany when people move house they take their kitchen with them. My brother-in-law went over to move his daughters Ikea kitchen into their new house. I was impressed that it could be dismantled and re-installed as when one watches kitchen fitters here they seem to smash everything they remove.
The Part P regulations has caused a problem for kitchen fitters and I think before Part P they did some very shoddy work which is likely why the Part P law was passed. The rules as to pre-made units with electric already installed allows non electricians to fit them and I would guess the kitchen fitters you had wanted to ensure they did not have to move any sockets and could use the pre-wired units.
It is currently Wed Jan 15, 2025 6:46 pm