Under Tub - outside all zones

Posted: Mon Jul 23, 2007 9:23 pm
by misterg
Hi

I've had conflicting advice on what can be put in under the bathtube. The sides cannot be removed without using a tool, so my understanding is this is outside all zones.

i'm lookin to get a shower pump fitted.

Can a socket be put under a bath for the pump, or should it be connected to an FCU outside the bathroom.

Also been told it can only be a low voltage pump - is this correct?

Cheers

Mister G

Re: Under Tub - outside all zones

Posted: Mon Jul 23, 2007 11:53 pm
by BLAKEY1963
[quote="misterg"]Hi

I've had conflicting advice on what can be put in under the bathtube. The sides cannot be removed without using a tool, so my understanding is this is outside all zones.

i'm lookin to get a shower pump fitted.

Can a socket be put under a bath for the pump, or should it be connected to an FCU outside the bathroom.

Also been told it can only be a low voltage pump - is this correct?

Cheers

MISTERG
IDEALLY ( OF COURSE YOUR PART P SPARK WILLADVISE )
I WOULD PUT THE PUMP UNDER THE BATH AND PUT THE
SUPPLY TO IT UNDER FLOOR BOARDSTO RCD SPUR OUTSIDE
BATHROOM. MOST OF THE THESE PUMPS ARE STEP DOWN VOLTAGES ANYWAY.
BLAKEY1963

Mister G[/quote]

Posted: Tue Jul 24, 2007 12:50 am
by misterg
Thanks Blakey.

If the ring main will be on the CU RCD, do I need another one, or will an FCU be sufficient?

Cheers

Mister G

Posted: Tue Jul 24, 2007 12:21 pm
by sparx
Hi, guess BLAKEYS working !! HI, Hi,
yup if ring on rcd then just FCU suffices, but under current regs [this year anyway] must take 4mm earth from FCU to local pipes, & as most pumps are placky link across incoming to outgoing pipes, regards SPARX

Posted: Tue Jul 24, 2007 9:20 pm
by Stephen the sparks
Under the tub is actually zone 0. Must be IPX7 protection, only 12v SELV equipment is allowed that cannot be reasonably located elsewhere.

No switchgear allowed in zone 0 I am afraid.

Regs 601-08-01 and 601-09-01 apply

Posted: Wed Jul 25, 2007 12:33 am
by misterg
[quote="Stephen the sparks"]Under the tub is actually zone 0. Must be IPX7 protection, only 12v SELV equipment is allowed that cannot be reasonably located elsewhere.

No switchgear allowed in zone 0 I am afraid.

Regs 601-08-01 and 601-09-01 apply[/quote]

Hi

I thought Zone 0 was in the tub and if you need a tool to remove side of tub then it is outside all zones.

Is this not correct?

Also what is IPX7?

Cheers

G

Posted: Wed Jul 25, 2007 12:39 am
by misterg
[quote="sparx"]Hi, guess BLAKEYS working !! HI, Hi,
yup if ring on rcd then just FCU suffices, but under current regs [this year anyway] must take 4mm earth from FCU to local pipes, & as most pumps are placky link across incoming to outgoing pipes, regards SPARX[/quote]

Cheers Sparx

Great that was what I was hoping for.

I'll make sure the electrician fits the 4mm earth too.


Regards

G