Hi,Could anyone tell me if there is a formula for working outhow many kitchen appliances or sockets are suitable to put on a radial circuit of 4mm cable.Would it allow more appliances on the circuit if it was made into a ring
Posted: Tue Jul 24, 2007 5:58 am
by thedoctor
See our project on radial circuits (Electrical) all the info is in there.
Posted: Tue Jul 24, 2007 12:05 pm
by sparx
Hi, a 4.0mm2 radial known as a type A2 can supply an unlimited number of outlets/appliances as long as the total floor area it supplies does not exceed 50M2 50[square]mtres.
regards SPARX
(this is becoming the circuit of choice over rings)