Too many sockets over too large area for protective device.

Posted: Tue Aug 07, 2007 8:56 pm
by I_spark
Hello,
The circuit is Sockets down 2.5/1.5 cable 8 points served (No ring) 15 A Bs 3036.
How can this problem be solved and rectified?

For sockets up again no ring 30 A BS 3036 2.5/1.5 3 points served it says too large protective device for cable size. How can this be solved and rectified?

Thanks in advance.

Re: Too many sockets over too large area for protective devi

Posted: Tue Aug 07, 2007 10:13 pm
by BLAKEY1963
[quote="I_spark"]Hello,
The circuit is Sockets down 2.5/1.5 cable 8 points served (No ring) 15 A Bs 3036.
How can this problem be solved and rectified?

For sockets up again no ring 30 A BS 3036 2.5/1.5 3 points served it says too large protective device for cable size. How can this be solved and rectified?

Thanks in advance.[/quote]

I SPARK
2.5 MM2 AS A RADIAL CIRCUIT CAN SERVE A FLOOR SPACE NOT EXCEEDING 50 M2 IF PROTECTED BY A 20 AMP PROTECTIVE DEVICE . TYPE OF CIRCUIT IS A2 FROM OSG PAGE 151