electric trip switch

Posted: Mon Aug 13, 2007 3:22 pm
by Ralph
I just have had a new conservary installed, which included 3 power points. As part of the new regulations the electrian tried to install a trip switch, between the main fuse box and the electric meter. The switch kepted tripping !!!. I pulled out all the plugs, but it still kept tripping. Any ideas what to do next.

Posted: Mon Aug 13, 2007 11:55 pm
by sparx
Hi Ralph, first of all don't blame the leckie! the RCD has just shown up a long standing problem which will need a leckie with an Insulation tester to find.
He will need to seperate all Neutrals from Consumer unit common bar to test each circuit in turn with all circuits switched off/fuses pulled, sorry but not really in the realms of DIY, but should not take long to identify 'duff' circuit[s], most often ring with earth touching Neutral, possibly skt fixing screw against cable, good sparky should find quite soon,
regards SPARX

Posted: Tue Aug 14, 2007 2:43 pm
by Ralph
[quote="sparx"]Hi Ralph, first of all don't blame the leckie! the RCD has just shown up a long standing problem which will need a leckie with an Insulation tester to find.
He will need to seperate all Neutrals from Consumer unit common bar to test each circuit in turn with all circuits switched off/fuses pulled, sorry but not really in the realms of DIY, but should not take long to identify 'duff' circuit[s], most often ring with earth touching Neutral, possibly skt fixing screw against cable, good sparky should find quite soon,
regards SPARX[/quote]

[color=red][/color]
Thanks, leckie found problem today, which was a double 3 point power switch. The wires were very loose, leckie spotted them, tighten up and trip switch works OK. The 3 point plug being used for a floor stand light, with no problems.

Took the two leckies 1.5 hours to find fault and re-store all plus etc.

Thanks