updating a consumer unit

Posted: Fri Aug 24, 2007 7:15 pm
by mirfield lad
Hi
I have a house which as been rewired (before I bought it) & the consumer unit has mcb's fitted. There is no earth supplied by the supply company and the earth is by the way of a spike into the ground.

I am selling the house and the purchaser as had a electrical check done and came back to say, this is not to the current standards, and needs rcds fitting.

So do the rcds need to replace all of the mcb's or can one be fitted inplace of the main switch. They said it would have to be a new consumer unit. Any help would be appreciated. Mirfield Lad.

Posted: Sat Aug 25, 2007 8:55 pm
by sparx
Hi, I am suprised to hear after a rewire that with a TT system (spike/rod)that there is no main RCD fitted as this has been a requirement for many years.
Either a 30mA in the 'tails' or in place of the main sw.
Or a 100mA type s time delayed one as above with individual RCBO,s for each power circuit, the dearest but best option if for yourself!
Regards SPARX

Posted: Sun Aug 26, 2007 7:11 pm
by mirfield lad
Sparx, thank you for all the information. I think I will go for the dearest option of 100mA type s & the indiviual RCBO's for each circuit.

Many thanks again.