Hello
I'm converting a horse box to bar, which will contain two chest freezers, Three double sockets and two lights. I'm using a garage cu with a 6a and 32a breaker. I'm finding it hard to work out the incoming cable I need for the unit. I believe I need a H07RN-F (BS EN 50525-2-21) cable which will have to run 25m from the generator. I'm thinking my design current is 2kw for each freezer, plus 200w for the lights and 39w for the sockets, so 18.5A. On 2.5mm flex its volt drop is 19, so (19x18.5x25)/1000= 8.7v. Is my design current correct? And if so then I should be fine with a 32a 240 plug and 2.5mm H07RN-F black cable?
Thanks for any help.