I am replacing my hut and need to transfer the electrics but want to add a second 2 gang socket. I currently have one 2 gang socket running directly off a small consumer unit. I want to add a second 2 gang back to back with the first (my new hut has two separate rooms and the sockets will be mounted on the dividing partition). Can I simple take a wire from each terminal in the current 2 gang directly to the same terminal in the second 2 gang?

Re: Replacing hut and transfering existing electricals

Posted: Sun Nov 15, 2020 11:07 pm
by Mr White
Providing the cable is the same size, and you are competent and you can test it, then yes.

Re: Replacing hut and transfering existing electricals

Posted: Mon Nov 16, 2020 11:55 am
by Philo
Thanks Mr. W

Re: Replacing hut and transfering existing electricals

Posted: Mon Nov 16, 2020 1:48 pm
by ericmark
With a overload under 25 amp in the main yes, not so easy in a house where likely using a ring final and a 32 amp supply, but with a radial supply no real problem.

However be aware not all outbuildings are wired as we think they should, I have seen a lovely garage consumer unit and really tidy wiring but on investigation found take as an unfused spur from a socket in the house with under size cable.

I even found a new build with 2.5 mm running length of house, then 6 mm SWA going from junction box to garage, so at garage one thinks that's OK 6 mm cable, then go to consumer unit to isolate and see on 10 amp MCB so remove lid to change and find only feeding 2.5 mm cable. Then found junction box and had to wire 6 mm SWA from junction box to consumer unit to up grade MCB. And this was not a DIY job, it was like that from new.

So inspection and testing is important, you can't assume.