Where to install fused spurs when adding double socket

Posted: Fri Feb 19, 2021 11:35 pm
by rob77
I currently have a double socket in my garage which is fed direct from the main consumer unit via an armoured 2.5mm cable. The socket then feeds into a fused spur to reduce the 2.5mm cable to 1.5mm cable to feed the garage light.

I am looking to add another double socket in the garage so intend to install a 13A fused spur prior to the existing first socket in the garage as all subsequent sockets will be protected by this fused spur.

My question is...since I will now have a 13A fused spur prior to the first double socket will I still need a second fused spur to reduce the 2.5mm cable to 1.5mm cable to feed my garage light?

Am I correct in concluding I will not need a second fused spur as the 1.5mm cable will be protected by the first 13A fused spur which protects the first socket?

Re: Where to install fused spurs when adding double socket

Posted: Sat Feb 20, 2021 10:31 pm
by Mr White
The FCU for the lights should have a 3 or 5 Amp fuse, it will not be there if you remove the FCU.