I have a shower in the bathroom connected to a 40 amp fuse in the mains box through an on-off switch with a red warning light, Just recently I have detected a smell coming from the switch when the shower is being used for a long period and the switch feels warm to touch. Is there likely to be a problem with the shower or does the switch need replaced ?
Thanks for any advice.
Re: Shower Switch
Posted: Fri Oct 05, 2007 7:45 pm
by BLAKEY1963
[quote="sasgps"]I have a shower in the bathroom connected to a 40 amp fuse in the mains box through an on-off switch with a red warning light, Just recently I have detected a smell coming from the switch when the shower is being used for a long period and the switch feels warm to touch. Is there likely to be a problem with the shower or does the switch need replaced ?
Thanks for any advice.[/quote]
SASGPS.
WITH CIRCUIT ISOLATED, INSPECT THE INSIDE OF SWITCH.
LOOSE CONNECTIONS CAN CAUSE ARCING AND OVERHEATING OF SWITCH TERMINALS.