MCB keeps tripping in new 10 way Schneider unit

Posted: Sun Sep 26, 2021 2:23 pm
by Spence1412
Just installed a new 10 way Schneider unit.
All ok apart from downstairs ring.
The circuit tests ok.
A mains powered radio and one table lamp work but any more than that and mcb trips.
I have unplugged all appliances and plugged them back in one by one but they all cause tripping.
If there was a short then the radio and lamp wouldn't work would they.
Very confused.
Kevin

Re: MCB keeps tripping in new 10 way Schneider unit

Posted: Sun Sep 26, 2021 9:19 pm
by Mr White
You said
Spence1412 wrote: The circuit tests ok.


What is "OK" and who tested it? and what was it tested with?

Picture of what trips would help.

Re: MCB keeps tripping in new 10 way Schneider unit

Posted: Sun Oct 03, 2021 9:36 pm
by chriscba
Swap the rings over to see if the fault moves to a different circuit.
Then if it has, you have an over sensitive MCB.
So you can change it

Re: MCB keeps tripping in new 10 way Schneider unit

Posted: Thu Oct 07, 2021 5:12 pm
by ericmark
I have a feeling it is not a MCB tripping but a RCBO or RCD?

I would guess wrong neutral, but as @Mr White says, who tested the circuits to show OK and how?

There should be an installation certificate showing test results, and either a compliance or completion certificate.