Replacing a 13 amp single socket with a fused connection unit
Posted: Sun Mar 03, 2024 8:58 pm
Good afternoon,
I currently have a surface mounted double 13a switched socket in my bedroom and 1 x surface mounted
13a switched single socket on the opposite wall.
I would like to change the surface mounted 13a switched single socket for a surface mounted switched
fused connection unit and spur with 2.5mm t&e to another surface mounted double 13a switched
socket next to it. From this double 13a switched socket I would like to spur 2.5mm t&e in plastic trunking
through a wooden timber door frame along the skirting board out to the landing area, here I would to
install a surface mounted 13a switched single socket. Would there be any issues, with this proposed new arrangement?
Thank you for assistance.
Kind regards,
Steve
I currently have a surface mounted double 13a switched socket in my bedroom and 1 x surface mounted
13a switched single socket on the opposite wall.
I would like to change the surface mounted 13a switched single socket for a surface mounted switched
fused connection unit and spur with 2.5mm t&e to another surface mounted double 13a switched
socket next to it. From this double 13a switched socket I would like to spur 2.5mm t&e in plastic trunking
through a wooden timber door frame along the skirting board out to the landing area, here I would to
install a surface mounted 13a switched single socket. Would there be any issues, with this proposed new arrangement?
Thank you for assistance.
Kind regards,
Steve