Using Diversity can 14.81kW range be installed to an existing 32A EN 60898 with existing 6mm T&E 15 metre run?
C/unit 100 Amp with 1 spare way and 45A-shower,2x32A ring,1x32Aradial
1x16A immersion,1x16A radial and 2x6A
10mmT&E/seperate C U enclosure or else?
Braniac/Anyone/Best solution much appreciated.Short of time!
Thanks.

Posted: Fri Nov 16, 2007 9:10 am
by kuzz
Give it a go. The cabe is protected by the 32A mcb anyway so you can't overload it. Just might mean cooking your beans then grilling your toast to stop it tripping!! Just joking, it should be ok.