Can anyone tell me how difficult/dangerous it is to fit an electric shower?
Also, does it make any difference that I'm replacing a 9.5kw shower with a 10.5kw one?
Posted: Thu Feb 28, 2008 1:05 pm
by kbrownie
hugo67,
Your design current will change, 9500w/230v=41.3A and 10500/230=45.7A and depending on the type of circuit protector you are using (mcb/fuse). It could effect the size of the cable to be installed. As you will need a 50A rated Fuse/mcb. Don't want to get to technical. But that's the problem with changing from 9.5 to 10.5kw.
As for dangerous, VERY if not correctly installed bathrooms are covered by part p of building regs and must be installed to comply with them. Not a DIY job really! you need a part p electrician.
Regards
KB
Posted: Thu Feb 28, 2008 1:21 pm
by hugo67
Appreciate the advice Ikbrownie, think I'll get someone in!