adding spur to cooker socket

Posted: Wed Mar 12, 2008 1:35 pm
by tereskan
My cooker is on its own ring main to the circuit box but is unused as we have a gas cooker and it is pugged in else where.

Seeing as the curcuit is unused could I use it to put power into a brick shed which backs onto my house, I plan to run 25mm cable from the socket into the shed into a 13A RDC FCU then into 2 double sockets?
I plan to drill directly through the back of the socket onto the outside wall of my house then though rigid conduit into the shed?

the only thing that will get powered for the sockets is a tumble dryer and maybe a light?

Posted: Wed Mar 12, 2008 10:13 pm
by sparx
Hi sounds a good plan but if still fused at 30/32A then should use 4mm2, to a 'garage unit' which has rcd & 1X16A + 1X6A circuit breakers fitted, ready to connect to sockets & lights,
NB this sounds like it may be 'Part-P' work if shed seperate from main house,
regards SPARX