Studying for my C&G 2382 I have been looking at sample questions. Most are easy, with some a little more hard to find for example A circuit supplying a socket outlet is protected by a BS 1361 fuse, the maximum permitted value of Zs is:- a. 1.77 Ω
b. 1.70 Ω c. 2.30 Ω d. 2.80 Ω here you need two regulations Table 41.2 gives the Zs but you need 411.3.3 to select 20 amp as below 20 amp RCD is used. But I have a couple I can’t find the answer for. 1) In a distribution circuit in a TN installation the disconnection time should not exceed:- a. 0.2 S b. 0.4 S c. 5.0 S d. 0.1 S without volts or A.C. or D.C. being declared I can’t find an answer have I missed something? 2) The insulation resistance value for a 230 V domestic installation when measured
between line and neutral conductors should be not less than:- a. 0.75 MΩ b. 2.5 MΩ
c. 0.5 MΩ d. 0.25 MΩ I get answer to 1.0 MΩ 612.3.2 Table 61 Page 158 but this option is not given. Again have I missed something? Also
Basic protection can be provided by
a. limiting the current which can pass through a body
b, ensuring all extraneous parts are at equal potential
c. automatic disconnection of the supply during earth fault conditions
d. separation of the supply and load by means of an isolating transformer.
I will guess on (a) but not sure if (b) could also be correct? Example of a) would be neon screw driver and b) earth free location. Any thoughts please?