Page 1 of 1
One Pipe Heating Sytem and HE Boilers
Posted: Fri Sep 19, 2008 6:47 pm
by bluegrahame
I have a "one-pipe" heating system and want a new high efficiency combination boiler.
My preferred Installer has said that the system should be converted to a "two-pipe" design.
Why is this? What will happen if I don't convert? can I damage my new boiler? and he's saying cost is about £3800. Does this sound expensive?
The property is a 3 bed, 6 radiator bungalow.
Thanks in anticipation.
Grahame.
Posted: Sat Sep 20, 2008 8:29 pm
by htg engineer
The one-pipe system will be fine with a combi boiler, but unlike the boiler they're not very efficient.
Are the radiators and pipework in decent condition ? maybe this is what the installer is referring to.
htg
Posted: Sun Sep 21, 2008 6:59 am
by Steve the gas
Hi,
I put a combi on a one pipe system - never again!!
It doesn't heat the house to any satisfactory degree,
I changed it to a two pipe -- perfect - roasting
But £3800 WTF
Re: One Pipe Heating Sytem and HE Boilers
Posted: Sun Oct 26, 2008 5:03 pm
by da pickles
[quote="bluegrahame"]I have a "one-pipe" heating system and want a new high efficiency combination boiler.
My preferred Installer has said that the system should be converted to a "two-pipe" design.
Why is this? What will happen if I don't convert? can I damage my new boiler? and he's saying cost is about £3800. Does this sound expensive?
The property is a 3 bed, 6 radiator bungalow.
Thanks in anticipation.
Grahame.[/quote]
if the pipework is in good order and the system is power flushed [ most manufacturers will invalidate the warranty if this is not done . allow £500]then there should be no problem as long as the return is kept below 50c
Re: One Pipe Heating Sytem and HE Boilers
Posted: Tue Feb 03, 2009 9:28 pm
by norwich-plumber
[/quote]
if the pipework is in good order and the system is power flushed [ most manufacturers will invalidate the warranty if this is not done . allow £500]then there should be no problem as long as the return is kept below 50c[/quote]
most manufacturers ask for the system to be cleaned not power flushed and the warranty will still be ok
Posted: Tue Feb 03, 2009 11:41 pm
by Dan2071
How do you powerflush a one pipe system? Doesnt the water just bypass the radiators?