Central Heating ,hot water radiator problem
Information, help and advice on many gas related subjects from gas fires to domestic appliances

3 posts   •   Page 1 of 1
dugit
Apprentice
Apprentice
Posts: 18
Joined: Mon Nov 15, 2010 11:39 pm

Central Heating ,hot water radiator problem

by dugit » Tue May 07, 2013 8:12 pm

Central heating when hot water system comes on so do the radiators
I have Glow Worm 80ff, Danfoss programmer CP715, Danfoss H series switching valve.
The radiator system works OK, but I notice that after a bath when the hot water system comes on the Danfoss valve goes to the middle position quite often (not always but usually) so that the radiators also come on and stays in that position even if I switch the radiators off at the CP715.
Is it the CP715 programmer faulty?

plumbbob
Project Manager
Project Manager
Posts: 1892
Joined: Wed May 07, 2008 10:59 pm

Re: Central Heating ,hot water radiator problem

by plumbbob » Tue May 07, 2013 8:37 pm

The first thing I would do is power down the heating altogether preferably when the valve is in the centre position.

Once the power is off, the valve should return to the heating off position with the cylinder coil side open. If it doesn't return then the valve is sticking. If it does return then operate it manually to ensure a smooth operation.

If that all checks out, then the possibility of a faulty timeswitch becomes more likely although there could be other possibilities such as a frost stat not working correctly.

archiej
Labourer
Labourer
Posts: 1
Joined: Sun Aug 04, 2013 9:08 pm

Re: Central Heating ,hot water radiator problem

by archiej » Sun Aug 04, 2013 9:34 pm

I have a Baxi 80 combi ECO,it works OK on the HW side but when I switch on CH the boiler just stops and start every few seconds,new PCB+gas valve(not checked)micro switch,new Venturi,new Temp.switch,but it still wont work.any ideas.

3 posts   •   Page 1 of 1
It is currently Tue Nov 26, 2024 10:47 am