15mm Gas Pipe Installation Limits
Posted: Thu Sep 27, 2007 10:34 pm
by JR656
What is the minimum distance a 15mm domestic gas pipe can be fitted to a hot water pipe? Are there any remedies if they are close eg. insolation?
Are there any other regulations regarding their positioning eg. electric cables, enclosed spaces?
Posted: Mon Oct 01, 2007 9:39 pm
by rosebery
Don't think so within the house. Think it's 8 inches if they are underground.
Rule of thumb might be how close are the gas and water inlets on your boiler?
Cheers
Posted: Sun Oct 21, 2007 2:50 pm
by Bay Plumbing
your gas and water need to be 25mm apart from and electrical cabling,and a clipping distance :
15mm vert-2m
15mm horiz-1.5m
22mm vert-2.5m
22mm horiz 2m
n.b between each clip.
gas supply out side:
375mm min depth if it under driveway or used fro heavy traffic area/min depth of 40mm under slabs or patio.
hope this helps you out,
Mark