Central Heating - change of pipe diameter

Posted: Tue Sep 02, 2008 9:07 am
by misterdun
Currently in my bathroom the central heating pipes (22mm) run underneath the bath but stick out into the room above the floorboards where I intend to put up a stud wall. The pipes stick out far more than required and want to move them. I am hoping to use pushfit fittings and speedfit flexible piping (15mm) which i have already bought to re-direct the pipes. Will the change in diameter cause problems or should it be okay?

Posted: Tue Sep 02, 2008 11:42 am
by htg engineer
What do the pipes feed ? if just one radiator then probably no problems. If it's the flow and return feeding the whole house then it needs to be kept as 22mm.


htg

Posted: Tue Sep 02, 2008 4:26 pm
by misterdun
Thanks for the reply. It is the flow and return so looks like I will have to spend a bit more money.