Air lock help

Posted: Thu Sep 11, 2008 2:12 am
by Snap
hi,

I changed the bathroom mixer shower tap. I turned off the tap by the cold water tap in the loft to stop the flow of water. After i changed the mixer tap and reopend the tap in the loft, there warm water started flowing ok however im barely getting any cold water in the bath mixer tap and the basin mixer tap is only putting out hot water and no cold water at all. The kitchen sink cold water has a good flow with good pressure so im guessing i have a huge air lock in the system.

With the bath having a mixer tap and the basin also a mixer tap, i dont know how to get rid of the air lock. Any ideas or help?

Thanks.

Posted: Thu Sep 11, 2008 9:32 am
by TheDoctor4
Hi

Have you had a look at the DIY projects area of this site, particularly the project on "Curing an air lock": https://www.diydoctor.org.uk/projects.htm This may be of some help to you.

Regards

Posted: Fri Sep 12, 2008 7:39 pm
by bobplum
are we saying the valve in the loft controls the cold water to the bath and basin and nothing else,if so the valve may the problem
bob

Posted: Fri Sep 12, 2008 9:44 pm
by htg engineer
Is the cold water to the bathroom tank fed, from the explanation it does seems this is the case. Is the cold water storage tank full, ball valve not stuck ?

Open the cold tap in the bathroom, insert a piece of hose into the outlet from the tank then attache the other end to the spout on the ball valve, lower the ball valve by hand and see if the water from the ball valve going down the hose will clear any airlocks.

Alternatively back fill from tap using a hose, but will have to be from mains cold water, electric shower ?

htg