Towel Radiator Valves

Posted: Mon Oct 13, 2008 5:01 pm
by AdAstra
I want to replace a radiator with a towel warmer/radiator and ordered two in line valves for the job from the radiator supplier. I was surprised to receive what appear to be two identical control valves for the job and not one control valve and one lockshield valve. Are lockshield valves not used in towel warmers? If not why not?

AdAstra

Posted: Tue Oct 14, 2008 1:34 pm
by plumbbob
Valves and lockshield valves are the same thing. What makes the difference is the application. One is used to control the on/off of the radiator and has a normal cap, the lockshield is used to balance the system by being left partially open. Usually they are fitted with a tamperproof cap, but not always as you can see.

Posted: Tue Oct 14, 2008 3:37 pm
by bobbych
A Towel warmer is just a fancy radiator. all rads should have a lockshield valve to prevent accidental changes therefor an unbalenced system

Posted: Tue Oct 14, 2008 6:54 pm
by AdAstra
Hi Plumbbob and Bobbych.

I will look around for a tamper proof cap.

I am also assuming that the four and a half turns needed to close my old lockshield valve if applied to the new valve will be ok to keep the system balanced.

Many thanks for the advice.

Adastra

Posted: Wed Oct 15, 2008 9:26 am
by bobbych
closing your lockshield V half way wont balance it. Its a starting point tho.