Posted: Fri Jan 09, 2009 5:08 pm
by SAM3
please can anyone help got combi boiler is overflowingfrom escape tube had new valve etc put in last winter also water coming out very little drips fr om some very small rubber tube on si de of boiler any help welcome also pressure up to 3.5
Posted: Fri Jan 09, 2009 10:08 pm
by htg engineer
Pressure too high, combi fill turned off ?
If so could be a problem with plate heat-ex or expansion vessel.
htg
Posted: Sat Jan 10, 2009 8:31 am
by Steve the gas
Hi Sam,
The small drips from rubber tube is prolly condensate from a condensing boiler- what is the make & model.
Is the filling loop disconnected- could be passing.
And as per Htg.