No Heating since new pump fitted

Posted: Sun Mar 01, 2009 11:49 am
by adman_lincoln
Hi I have just fitted a new circulating pump and now the boiler only fires for a few mins.

I have made sure I have fitted it the right way followed venting procedures and bled the radiators.

The pump works but the hot water only seems to get to the 3 way valve then the boiler gives up. The position on the valve moves when switched between water and heating and it worked fine before pump replacement.

The reason for replacing was noise.

Any help with this would amazing.

Thanks

Posted: Sun Mar 01, 2009 2:55 pm
by plumbbob
The logical explanation is you still have air trapped in the pipework which is preventing the flow. Either crack a joint open to let out water and the air plug, or consider popping the pump in backwards temporarily to shift it.

Posted: Tue Mar 03, 2009 11:23 am
by tomkev1
IT is well worth checking that you have fully opened the pump valves and not closed them.I.E that is open them in the same direction as you would a normal tap.I once had a plumber/gasman workmate of mine make the same simple mistake, took him ages to find the fault.

:oops:

[/u]

Posted: Tue Mar 03, 2009 4:58 pm
by htg engineer
Try venting the pump.


htg

Posted: Tue Mar 03, 2009 7:03 pm
by adman_lincoln
Hi thanks it turns out I'm all bunged up with slugde!!! So now in the process of flushing the system. Either that or pay £500 to a plumber!