double panel radiator problem

Posted: Wed May 12, 2010 8:44 pm
by chad52
im sorry if this question has been asked before but i cant se to find in forums.i had my walls replastered back to the brick and two double panel radiators had to be removed.when the radiators were put back on i found later that only one panel of the radiator filled up on both of them.if i try to bleed the other panel on each i hear no hissing so obviously its not filling and i dont know why.can anyone help me to correct this problem.many thanks
chad


brill problem solved and yes it was blockage of bleed screws on both radiators as guys who removed did indeed store them upside down which caused problem.many thanks to all who have helped me and most of all to this site who gave me the technical support i needed.
brill thx so much again.
chad

Posted: Thu May 13, 2010 9:38 pm
by Barry Bunsen
Hi
Incredible coincidence to have the same problem on 2 separate radiators. I assume each rad has 2 bleed screws - one for each panel - but only one on each rad seems to function. I assume the full panels are pressurised. Do the full panels actually heat up and if so is any part of the unbled panels heated?

Posted: Thu May 13, 2010 10:51 pm
by chad52
Barry Bunsen wrote:Hi
Incredible coincidence to have the same problem on 2 separate radiators. I assume each rad has 2 bleed screws - one for each panel - but only one on each rad seems to function. I assume the full panels are pressurised. Do the full panels actually heat up and if so is any part of the unbled panels heated?


both rads were took off wall same time put back about three mths later by guys doing plastering.yes the rads have two bleed screws and only one will hiss and fill giving heat the other does not fill at all so no heat on that one panel.i dont know about pressurising or how to do so.my heating works from combi boiler and thx much for replying to my problem
chad

Posted: Fri May 14, 2010 2:06 pm
by Dave From Leeds
Hi Chad,

You could perhaps try sutting off all of the radiators except one of the two problematic ones. Then try bleeding the cold panel again. If that works, do the same for the other one.

As Barry says, it seems a coincidence for two of them to do the same thing. It could be that the bleed valves have somehow become blocked.

Posted: Fri May 14, 2010 6:42 pm
by Barry Bunsen
Hi
By pressurising I simply meant filling with water at the same pressure as the rest of the heating system. Clearly one panel on each rad does pressurise and the other does not. I can only think there is a blockage on each one. You could try removing them again and flushing out with a hosepipe in the garden. Completely take off the bleed valve if you do this and check it isnt blocked (you could try this with the rads in situ but it could go pear shaped if you cant get the valve back on and the rad starts filling!)
Depending on their age it could be new rad time. At least you have the Summer to think about it.
Good luck.

Posted: Sat May 15, 2010 6:44 pm
by htg engineer
Turn off both radiator valves, remove the radiator vent nipple fully.

Insert a pin/needle into the vent point, be prepared for a little water - dust sheet and a quick hand - re-instating the vent nipple required.


htg

Double radiator

Posted: Mon May 17, 2010 1:40 pm
by harberg
Hi
I would think that just like everybody else you stored the radiator upside down to avoid the black water sitting at the bottom spilling onto the carpet.
This will probably have blocked the bleed hole. A pin will do the trick!

Posted: Mon May 17, 2010 6:27 pm
by chad52
Dave From Leeds wrote:Hi Chad,

You could perhaps try sutting off all of the radiators except one of the two problematic ones. Then try bleeding the cold panel again. If that works, do the same for the other one.

As Barry says, it seems a coincidence for two of them to do the same thing. It could be that the bleed valves have somehow become blocked.



excellent advice and although my heart jumped when i pound problem it has saved me a few quid getting a heating engineer as it was a bleed valve blockage and when i inserted wire to test the amount of air escaping startled me thx so much dave
chaq

Posted: Mon May 17, 2010 6:29 pm
by chad52
htg engineer wrote:Turn off both radiator valves, remove the radiator vent nipple fully.

Insert a pin/needle into the vent point, be prepared for a little water - dust sheet and a quick hand - re-instating the vent nipple required.


htg


thank you so much this did indeed prove to be the cause and has saved a big headache for me and expense boy did i jump when air came out after removing blockage
cheers
chad

Posted: Mon May 17, 2010 6:31 pm
by chad52
Barry Bunsen wrote:Hi
By pressurising I simply meant filling with water at the same pressure as the rest of the heating system. Clearly one panel on each rad does pressurise and the other does not. I can only think there is a blockage on each one. You could try removing them again and flushing out with a hosepipe in the garden. Completely take off the bleed valve if you do this and check it isnt blocked (you could try this with the rads in situ but it could go pear shaped if you cant get the valve back on and the rad starts filling!)
Depending on their age it could be new rad time. At least you have the Summer to think about it.
Good luck.


thank you barry for the help you gave me and i will earmark your words for future use if needed it was a bleed valve blockage on both radiators and back up and running again
thank you
chad

Posted: Mon May 17, 2010 10:17 pm
by Dave From Leeds
Chad,

Thanks for getting back to us. It's so frustrating when we never find out whether advice has been of any use. Glad you sorted the problem.

Re: double panel radiator problem

Posted: Sun Nov 16, 2014 11:34 am
by jonboy123
Thanks a lot for this guys. Just about to go buy a new rad as could't figure this one out.