expansion vessel
Posted: Sat Dec 11, 2010 2:18 pm
by John Paul
I have 4 rads weeping in a two story house downstairs,The system is gas operated and is sealed.as there is apressure gauge set at 2bar in the hot press.I dont seem to be able to locate an expansion vessell.Can I still go ahead drain off the system and repair the valves.
Regards john paul
Posted: Sun Dec 12, 2010 4:28 pm
by plumbbob
Yes you can.
The pressure vessel is probably integrated inside the boiler.
When you re-fill, only fill to between 1 and 1.5 bar. 2 bar is a little on the high side and will be putting unnecessary strain on the system fittings.
Posted: Mon Dec 13, 2010 1:50 pm
by John Paul
[quote="plumbbob"]Yes you can.
The pressure vessel is probably integrated inside the boiler.
When you re-fill, only fill to between 1 and 1.5 bar. 2 bar is a little on the high side and will be putting unnecessary strain on the system fittings.[/quote]
Thank you, once again