Posted: Sun Aug 16, 2020 3:42 pm
by happyatom
We have a Baxi combi boiler which was working fine and then, without any changes to the system, there are not 3 different scenarios:
* some taps and showers run intermittently hot and cold
* there are 2 taps which run perfectly OK
* 1 tap which doesn't trigger the boiler to start at all

Seems like a flow problem - so we had the flow switch replaced. Same issues.
Changed the heat exchanger - same issue.

The water pressure is good and the flow from all taps, even the one that doesn't trigger the flow switch, is good.

The boiler was serviced within the last couple of months.

Our plumber is at a loss to know what the issue can be - has anyone had similar problems and found a fix?

Thanks for any thoughts / guidance.

Re: Baxi combi boiler flow problems and running hot then cold

Posted: Mon Aug 17, 2020 9:47 pm
by stoneyboy
Hi happyatom
Suggest you contact Baxi and get one of their engineers out.
Regards S

Re: Baxi combi boiler flow problems and running hot then cold

Posted: Thu Aug 20, 2020 10:29 am
by happyatom
Thanks for the advice - I followed it and fixed within 20 minutes!

In case anyone else having similar issues, it was the Flow Regulator causing the issues - there was some confusion between flow switch and regulator when our original plumber was speaking with Baxi support and we got the wrong part.

Expensive though as we had to sign up for a year!