Hi all - new here, just asking a couple of questions to make sure I am not over reacting to some work I have had done which I feel is below par.

Screenshot 2021-06-16 at 20.50.18.png
Screenshot 2021-06-16 at 20.50.18.png (149.61 KiB) Viewed 1696 times

Speedfit pipe has been laid very close to floor board level - so much so that the floorboards are sitting directly on the clips - surely this cannot be right?

pipe_bend.jpg

Also, some pipes have been routed underneath some trunking and then sharply bent upwards where they go into a 90deg pushfit bend fitting at a bit of an angle. My take on this is that it is not only placing stress on the pipe/fitting, but that it also is pressing down on the plasterboard ceiling below (a ceiling board which we will be taking down and replacing shortly - at which time I think this pipe will 'spring' out due to the pressure of the bend and may then be difficult to refit the board).

Would welcoome any thoughts on this, thanks.

Re: Plastic pipe standards and floor boards sitting on clips

Posted: Fri Jun 18, 2021 10:33 pm
by stoneyboy
Hi masmith
Jguest suggest installing pipe through the neutral axis of joists, they do not comment on notching as an installation method. The minimum bend radius for 15mm pipe is 175mm.
Regards S

Re: Plastic pipe standards and floor boards sitting on clips

Posted: Mon Jun 21, 2021 9:25 am
by masmith
Hi Stonebiy - thanks for the reply - v helpful - This is 22mm pipe - any idea what the min bend radius is for this? thank you

Re: Plastic pipe standards and floor boards sitting on clips

Posted: Tue Jun 22, 2021 11:35 pm
by stoneyboy
Hi masmith
Minimum bend radius for 22mm pipe is 225mm.
Regards S