by ericmark »
Mon Dec 31, 2007 7:04 pm
I think we are looking at inrush?
When any motor starts it uses a lot more power than when running, fuses and MCB's are rated to allow for this. In fuses we have motor rated with an M and second figure and with MCB's type 4 or D depending on age. There are systems to help this form the star delta on three phase supplies to auto transformers softstarts and inverters. As to which to use is dependent on how and where it is used. Yes a 16 amp supply will help. But also a motor rated 13 amp supply could also work. One problem with motor rated supplies is the earth loop impedance required also changes it is not as simple as just changing the MCB. If it has one location then upgraded supply may be the answer but if used in multi locations then a softstart unit may be required. Softstarts and Inverters both allow the item to start slowly so reducing the inrush but inverters also allow speed variation and are more freely available. you really do need an industrial electrician to advise. The house electrician will not be familiarly with these specialist items. Same with suppliers you need someone who supplies industry not the domestic trade to advise you.
All best Eric