If the join is to be plastered over then you are not allowed to use anything that uses screws to grip the wire. hager make a special junction box which has push in connectors with some spring clip arrangement which is allowed. Also it is common to crimp the cables and cover with shrink sleeve with epoxy resin on inside or self amalgamating tape then normal tape over that. In other words a water proof covering so if wall ever becomes wet no water can enter joint.
The old round junction box is not permitted as it uses screws to grip cables.
526.3 Every connection shall be accessible for inspection, testing and maintenance, except for the following:
(i) A joint designed to be buried in the ground
(ii) A compound-filled or encapsulated joint
(iii) A connection between a cold tail and the heating element as in ceiling heating, floor heating or a trace heating system
(iv) A joint made by welding, soldering, brazing or appropriate compression tool
(v) A joint forming part of the equipment complying with the appropriate product standard.