by onimpulse » Tue Jun 01, 2010 1:05 pm
by eggers » Mon Jul 05, 2010 10:41 pm
by onimpulse » Tue Jul 06, 2010 4:48 pm
hi, the boiler starts with a bangeggers wrote:does the boiler start with a bang or does it start to bang later on?
by eggers » Tue Jul 06, 2010 9:42 pm
by onimpulse » Wed Jul 07, 2010 12:54 pm
hi thanks ,the boiler was serviced in january . i will get him to come back and have a look! will let you know ... thanks againeggers wrote:oops, sorry i thought you meant the HE baxi solo, they bang all the time because of poor electrode design :oops:
hmmmm, well, when was it last serviced?
i don't think it would be a problem with the pilot, like a blockage or anything like that. I don't think it would be a pcb fault as the solo 2's light the pilot first then go to main burner.
it could be a gas valve fault, lighting at a higher rate or possibly a crack in the burner.
by eggers » Sat Jul 10, 2010 11:29 pm
by htg engineer » Sun Jul 11, 2010 9:43 pm
by onimpulse » Mon Jul 12, 2010 10:17 am
i wll do that and thanks for your input !eggers wrote:please do send a reply, i would be curious to know what the fault was, just in case i come across this fault too
by eggers » Tue Jul 13, 2010 4:34 pm
htg engineer wrote:It could just be a dirty pilot or burner, if the pilot flame is small and not close enough to the burner you may get explosive ignition. Same will happen if the pilot is fine and the burner is partially blocked.
htg