by ericmark »
Tue Oct 19, 2021 9:20 pm
I had a clamp-on ammeter supplied by Scottish power calibrated in Watt hours and watts, it was to be clamped around the tails to the consumer unit, however monitoring all was rather pointless, as you could not work out what was using the power.
I also have some plug in devices, and they do have their uses, [attachment=0]Caravan-battery6_28-06-20.jpg[/attachment] this shows battery charger recharging caravan battery.
But in the main no useful data if I want to know how much power a bulb uses, it is written on the bulb.
I had two fuse boxes in last house each fed from a RCD, and when one tripped I lost two freezers full of food, so this house all RCBO which is the MCB and RCD combined.
The RCD comes at 4 types AC, A, F, and B, but the RCBO as a single width device comes as either type AC or A, so if you need type B then can't really use RCBO's.
The distribution unit used for domestic is type tested and have a maximum of 120 amp, in real terms 100 amp, the old Wylex fuse box main isolator was only rated 60 amp, so most home have a supply of 60 to 100 amp, there are the odd ones with split phase or three phase but these are rare.
EV charging points often require a type B RCD or a DC monitoring device to turn off supply should it exceed 6 mA, and depending on the earth type it also may need to turn off supply then earth if voltage not between 207 and 253 volt, also with solar panels often needs to turn them off if not between 207 and 253 volt.
So with a TN supply may need the special cut-out, and with TT supply special RCD's. Also with TT you may need double pole RCBO's and I know Wylex make them, but does not seem that fusebox makes them.
So there can be a huge variation in price with TT and TN, fusebox SPD can be as cheap as £35 but Wylex more like £100.
Also a huge variation in price of RCBO's fusebox down to around £15 but some can cost up to £35.
In the main it is a compromise, but some one needs to sign they have designed it all.
-