I have read that it is dangerous,when bonding in a bathroom,to connect it back to the consumer unit. Just wondering why its dangerous.
Thanks Techmad.

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Wed Jun 27, 2007 8:13 pm

Hi techmad, you create a zone of equal potential across all exposed metal in the area, which is fine. If you then run a main earth back to the con. unit the theory is if a serious fault occurs on a different circuit the voltage on the external earth wiring could rise considerably before the protective device operates to cut off the faulty circuit,that voltage could then appear on bathroom earthing. It would need at least 2 faults simultaneously to occur for it to be a problem, but it's poss.
The new 17th edition look at this in different way, like continentals no more bonding in bathrooms/kitchens, but all circuits in area Must be on RCD's
regards SPARX

Techmad
Labourer
Labourer
Posts: 4
Joined: Thu Jun 21, 2007 3:14 pm

bonding in bathroom

by Techmad » Fri Jun 29, 2007 10:26 am

Thanks sparx, Im just reading a few books on domestic wiring and have come across some things such as this ,which im not really clear on. Thanks again Techmad.