by sparx »
Mon Dec 26, 2011 4:05 pm
Hi, just back myself so catching up with posts.
Agree with Ericmark as usual, make 2-20A radials poss. best answer, making sure unused link made safe from accidental contact in outlet boxes.
As for 'borrowed Neutrals' on lights, imho leave as 2 circuits - no problems as long as both on same RCD half of board.
Only really an issue if using all rcbo's then no easy way other than making as one circuit.
Can understand his reluctance to spend time finding ring fault at the time of board change if he was booked up every day.
I have recently had same problem, since I allow one day for board change, including any earth upgrades needed and to complete test sheets as I go;
no time to find 'open ring' but don't want to issue test cert with 'failures'. went back a few days later and owner had remembered a half done extension to ring in loft for aerial amp. and put back as original, circuit tested fine!
Insist on cert even if with exception comment to kitchen circuit then another sparks should be happy to do remedial work and issue a minor works cert.
First company can also register job with LABC even with exception on cert.
regards Mac-Sparx