C2 fault of lack of continuity one would assume earth continuity as clearly if line or neutral it would not work, unfortunately there are some cow boys doing EICR's so often as electricians we are scratching our heads wondering what they saw.
But a plug in socket tester with loop test will cost around £40, cheaper ones don't have loop test, and you really need the loop test, the loop test checks the earth is good enough, without loop test it may show an earth is there, but it may be inadequate, so google "Socket tester with loop" select on and test.
Oh and washing machines are not light load, they together with tumble driers are likely the heaviest plug in load you can get in the home. The IET/BSi in their regulation book in the back suggest a non portable appliance with over a 2kW load should have a dedicated supply, this would include ovens, washing machines tumble driers and immersion heaters, in practice immersion heaters do normally have a dedicated supply, and some times also ovens, but rare for laundry equipment, it is not only the power used, but for how long, so a kettle may be 3 kW but runs for 6 minutes, a tumble drier 2.2 kW but runs for an hour, the immersion heater 3 kW runs for 3 hours.
I don't have a dedicated supply for my washer and tumble drier, but I am well aware a high load.