Hi Eric, an oft argued point,
The regs are not absolutes of course but a guide in the same way as the highway code interpretates the motoring law for us mere mortals.
We are all quite at liberty to design any circuit set up we want as long as we are prepared to show by calcs. how they are safe.
To save us having to do constant designs for basic, oft used circuits, the IET have published 3 domestic only standard circuits called A1, A2, & A3 types which we know as a Ring, & 2 types of radial. These circuits have set parameters that are to be encompassed. They have calculated that if all the rules for these are followed to the letter then "no further calcs. are required".
This does not allow us to pick bits from it as we see fit, so by default the arrangement suggested DOES NOT COMPLY!
There is also no need to put the overload device at the origin of the circuit provided it is a short distance from source to protective device, no tees off it and unlikely to sustain mechanical damage, eg a panel meter reading bus-bar volts on a 1000A bar can and often is fed by a piece of 1.5mm2 without fusing at all until a panel mounted fuse holder next to the meter!
Another such example given at an IET Inspect/test course was a FCU fed from a socket on a ring to a spur of 1.5mm2 to a fixed appliance, the short length between socket and FCU can be in 1.5mm2 as long as short & unlikely to be damaged.
I must agree it is difficult to find such stated in the regs & in a quick check I can only find conditional ref. in a note to reg. 536.1 pg. 116
So you are correct and unless using 4mm2 on 32A, then 2.5mm2 should be classed as a type A3 radial, fused at 20A.
N. B. in red book appendix 15 (informative) page 363 there is a 'cut-&-paste' typo in top box, top line says 'A radial final circuit starts AND FINISHES at the dist bd.......
The capitalised words above should be deleted in your books.
Finally the supply to the house is outside the scope of the IET regs and is covered under the 'Electricity, Safety, Quality & Continuity Regulations 2002,
Get person insisting on you deviating from the regs. to sign the non-compliant installation Cert. as I wouldn't and it would fail a later P.I.
regards as ever SPARX