by sparx »
Mon Sep 14, 2009 8:21 pm
Hi, Excuse the pun but there is no EARTHLY reason to connect an earth wire to ANY back box if wiring is in twin/earth! the Earth wires called CPC's should go direct to the earth terminal on the socket!
The unnecessary and in my view undesirable practice of crowding an unrequired wire in a cramped box is a piece of folklaw perpetrated by numpties at the NICEIC on their members.
This originates from a mis reading of reg.543.2.7 which says :
where using the earthed metal work of a wiring system such as conduit,trunking, steelwire armouring as the CPC then a wire shall be connected to bring the earth FROM the box TO the accessory, not vice-versa.
So in answer to your question connect CPC from donor socket to new sockets earth terminal, you can't earth a plastic box!
regards SPARX