Hi Bluto,
You won't get an answer from a DIY shop assistant, they are not qualified to answer and so are discouraged from doing so in case they mislead some one & the store gets sued!
I agree with the others, the wiring should go to the face plate whether its plastic or metal clad since it is the earth pin that needs connecting plus metal plate if fitted.
As for 'pigtail' earth to back box, again only required if system of wiring uses metal conduit for it's earth, nowadays only found on older houses, usually local authority owned.
for those with the 'big red book' to look at 17th ed. regs 543.2.2(vi),
543.2.7 apply,
personally I don't fit 'pigtails' into an already crowded box,
regards SPARX