by kbrownie »
Tue Mar 03, 2009 8:11 am
Hi Impope,
Firstly, Is the upstairs circuit on its own breaker from the consumer unit? This means the downstairs has it's own breaker too and these are two circuits are seperate.
Secondly, Has any work has been carried out that could have damaged cables? (nails, screws in to walls etc..)
Thirdly, is there no earth readings at all upstairs sockets.
I am assuming the re-wire did have all CPC (circuit protective conductors installed) Earths that is!
So start back at the consumer unit to check that the cpc/earth has not come loose and the terminal is tight within the earth bar. then socket by socket (upstairs) checking at First socket in the circuit working to last for loose connection.
Most faults can be found at the accessories.
Remembewr to isolate the circuit before inspection and prove the circuit is dead. I'd isolate whole system whilst you are inspecting at consumer unit.
Kind Regards
KB