Moby1,
If you can carry out the tests you can issue a minorworks certificate.
Tests are:
Earth continuity, Polarity, Insulation Resistance, Earth fault Loop Impedance, RCD rated current. I also include operation checks on RCD as if completing an Installation certifcate.
If you have a friendly electrician they can carry out the tests for you.
ban_all_sheds,
Surely this is a question of assessment for the installer, if a piece of equipment has operated for years and it's replaced by an identical piece of equipment, how can the cable be inadequate (no I'm not suggesting a 7kW shower fed by 1.5 T&E should be ignored). Say the cable was installed to comply with the 15th ed, chances are it certainly won't comply with the 17th ed but there is no requirement to upgrade a circuit to the 17th when carrying out repair,replacement or maintenance work.
If the shower has been installed on a dedicated circuit without an RCD then one should be fitted but if a 32A MCB is replaced with a 32A RCBO does this constitute a modification to the fixed wiring?