external light
Ask questions and find answers to many subjects relating to electrics and electrical work

9 posts   •   Page 1 of 1
carlos edwards
Labourer
Labourer
Posts: 1
Joined: Sat Nov 24, 2007 9:24 pm

external light

by carlos edwards » Sat Nov 24, 2007 9:29 pm

trying to replace an old external light
coming out of the wall there are 2 red wires 2 black wires and 2 bare wires ( presumably earth????)

i fastened the 2 red wires up to the live connector
the 2 black wires up to the neutral

and fastened the 2 bare wires into a connector

light came on but as soon as i tried to turn it off at the switch it blew the fuse??????

help please!!!!!!

BLAKEY1963
Site Agent
Site Agent
Posts: 684
Joined: Wed Jun 13, 2007 11:57 pm

by BLAKEY1963 » Mon Nov 26, 2007 8:52 am

carlos edwards.
this is part p work and notifiable , and not diy.
get in a part p reg sparky .

BLAKEY1963

markj81
Labourer
Labourer
Posts: 2
Joined: Sun Dec 16, 2007 2:17 pm

by markj81 » Sun Dec 16, 2007 2:21 pm

I have a related question to this...

The house we bought (5 years old) has a fitting for an external light, we've bought a ligh and i was going to fit it but once uncovering the wiring I was faced with 1 red, 1 black and what appears to be copper wire.

With the fitting needing earth, live and neutral, is this fitting safe to fit as it is or does something need to be done first?

rflight
Tradesman
Tradesman
Posts: 32
Joined: Sat Dec 15, 2007 9:05 pm

by rflight » Sun Dec 16, 2007 8:11 pm

Blakey, this is not notifiable works to part P.

Sounds like you have a pemanent live and switched live mixed. What were the original connections on the old fitting. You might need a multimeter to find out what connections you have.

Mark, is this twin and earth cable, if so then the bare copper wire is an earth and needs earth sleeving. It should be ok to use.

Check the how to section for more advice

markj81
Labourer
Labourer
Posts: 2
Joined: Sun Dec 16, 2007 2:17 pm

by markj81 » Sun Dec 16, 2007 9:47 pm

I've checked the 'how to' section and found it didn't really help with this question.

Dumb question (well possibly) what do you mean by putting the sleeve on? Do you mean covering the bare copper wire with the earth green and yellow sleeve?

I wouldn't know if its twin.

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Sun Dec 16, 2007 10:26 pm

carlos,
the 2 reds go together in a spare term block not connected to the fitting, the 2 blacks go to the lights brn. & blue wires, one to each, the bare ones should be sleeved/taped grn/yel and connected to the earth term. on light.
the 2 blacks are one Neutral & one switched live, which should have red sleeving/tape but often missing. with a B.C. lampholder or a modern ES type it makes no difference which way round you connect it, regards SPARX

rflight
Tradesman
Tradesman
Posts: 32
Joined: Sat Dec 15, 2007 9:05 pm

by rflight » Sun Dec 16, 2007 11:02 pm

[quote]fastened the 2 red wires up to the live connector
the 2 black wires up to the neutral [/quote]

If the two black wires are live and neutral then the fuse would have blown at switch on.... not switch off.

333rocky333
Ganger
Ganger
Posts: 182
Joined: Sun Nov 25, 2007 11:03 pm

by 333rocky333 » Sun Dec 16, 2007 11:34 pm

I would add its good practice to always have the centre contact of the es holder as live.

Will then ensure to conform to reg 553-03-04.

sparx is right to a point it's not always compulsory,but you cannot be certain the lampholder on some cheap foreign fittings, is to bs standard and would be safer if the bulb ever shatters exposing the metal casing or you touch the thread screwing the lamp into a non bs edison screw holder.

rflight
Tradesman
Tradesman
Posts: 32
Joined: Sat Dec 15, 2007 9:05 pm

by rflight » Mon Dec 17, 2007 7:30 pm

Yes mark, earth sleeving. Connect to light fitting and let us know what happens.