by ericmark »
Mon Jun 14, 2010 12:40 am
“Hi
Would the following be legal. (after the quick description of the current set-up)”
It could be but at a cost you may not want to pay
”A new rewire has been under taken by qual Elec.
A New Consumer Unit has been instaled, split load, there are two non-rcd covered circuits.
But the 2ring set up (up / down stairs) has a small problem when I repair computers which casuse the RCD to fail I have to go to the celar to reset it and as it also has the TV and other units with clocks which have to be reset and Sky boxes .”
314 DIVISION OF INSTALLATION is the regulation covering this. It is a problem for electricians as it says “reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced by equipment in normal operation” but it does not define normal.
”Can I install a ring main 32A 2.5mm cables to two radial curcits with their own 16a/rcd seprate curcit in a small room over a desk length of about up to 4 meters in length..
each "16a/RCD" unit in would have 3 or more double sockets in 100x50 Tower trunking. Marked with warnings about max current for the set of sockets.
Many Thanks for your comments.”
This could be one method. However there are some problems with it not least you need to run cables from the consumer unit and if these are buried in the wall you will need to use Ali-tube cable, plus the problems in complying with Part P.
Computers do not draw much power and so isolation transformers can likely do the job with a lot less outlay. You will likely be able to get a 750kva transformer for under the £100 you would need to pay the local council building control for permission to do the work which will deliver 3A which is likely enough to power a PC.
The UPS (Uninterruptable power supply) come in two flavours. Those, which isolate, and those, which during normal operation have a direct connection. The former will do what you require.
As to the safety of that supply you have a number of options. Using an isolation transformer for a single item you may consider no earth is best option, or centre tapped earth, or RCD. I would personally use an RCD. I have had problems in the past with centre tap because the fuse is often only fitted in line not neutral. In fact our benches had 10ma RCD’s fitted to sockets our thoughts were if it trips a 10ma RCD then the power supply is destined for the bin as likely to cause problems in the field.
Earths in a workshop are of course considered as part of the risk assessment, and there is a big question mark about the use of anti-static mats, and wrist bands, because they can give the user lethal shocks. I know in the university very regular checks were made as to the earth loop impedance, and you, will as a place of work, come under the Electricity at work act. Even if self employed. It is considered that the strap should be connected via a 1M ohm resistor which is large enough to stop lethal shock but small enough to leak away static.
However this is not a DIY question and really you should be posting on something like the IET forum which is designed for the more technical questions.